Power Surge

Post by Dibsy »

Had a power surge today batteries down to 55 % at 730 full by 11 30 . :D . 400 amp batterie

Dibs
User avatar
BruceS
Site Admin
Posts: 9305
Joined: Thu Nov 22, 2012 7:32 pm
Location: Mannum, SA, 5238
Has thanked: 36 times
Been thanked: 36 times

Re: Power Surge

Post by BruceS »

Imagine pumping it into Lead batteries like that?
Good stuff!
*******************
BruceS
Mannum, SA

********************
User avatar
T1 Terry
Posts: 15965
Joined: Fri Nov 23, 2012 3:44 pm
Location: Mannum South Australia by the beautiful Murray River
Has thanked: 50 times
Been thanked: 30 times

Re: Power Surge

Post by T1 Terry »

Around 180Ah in 4 hrs, and I'd imagine the solar wasn't at its best until after 9 am so the last part must have been going in at a fair rate. So what are you going to do with the other 5 hrs of solar energy, run the air con or heat the water.... or a bit of both? You never had these problems with the old batteries did you, maybe they are just too much trouble with all these other things you have think about now :lol:
Haven't melted any more fuses of fuse holders on the solar input? You know it's getting serious when you blow a 50 amp fuse due to over load ;)

T1 Terry
A person may fail many times, they only become a failure when they blame someone else John Burrows
Those who struggle to become a leader, rarely know a clear direction forward for anyone but themselves
Dibsy
Posts: 81
Joined: Tue Sep 27, 2016 10:41 am

Re: Power Surge

Post by Dibsy »

Oi terry that was a 60 amp fuse that let go .

Dibs
User avatar
T1 Terry
Posts: 15965
Joined: Fri Nov 23, 2012 3:44 pm
Location: Mannum South Australia by the beautiful Murray River
Has thanked: 50 times
Been thanked: 30 times

Re: Power Surge

Post by T1 Terry »

1100w of solar through a PWM controller, the experts will tell you the very best you could get is 70%, 1100w x 0.7 = 770w divided by 13.4v as an average between the 13v and 13.8v range the battery would have been at while charging = 57.46 amps, even at 13v that's only 59 amps so how could that melt a 60 amp fuse........ unless their 70% figure is wrong and you really can get more than 70% efficiency through a PWM controller..... bugga, that would wreck a whole lot theoretical scribbling and certainly not suit the MPPT choir :lol: What is the highest charging amps you have seen Officer Dibble?

T1 Terry
A person may fail many times, they only become a failure when they blame someone else John Burrows
Those who struggle to become a leader, rarely know a clear direction forward for anyone but themselves
Dibsy
Posts: 81
Joined: Tue Sep 27, 2016 10:41 am

Re: Power Surge

Post by Dibsy »

O mr terry you do have a way with words .on another note I put bigger vents both ends of the batteries with 2 75 ml fans with a thermal switch. 30 c is to low it dosnt turn of so I bout a 40 c of flee bay .

Dibs