Triptrackstriptracks wrote:Kappy,Kappy wrote:Good Morning.
Comments noted, will need to relocate invertor back to where it was, seemed like a good idea at the time.
240 Volt isolated by manual switch.
Seems my victory was maybe premature.
Well last night I ran A/C for about 3 hours and when turned off was showing 90%.
So over night I was running electric side of Suburban HWS, microwave on standby, 2 TV's on standby and 24 volt fridge and this morning before the sun had any effect on panel, notice an alarm coming from Bus.
On inspection invertor fault light was on and controller was showing 0% nothing coming in and nothing going out Amp wise but was displaying 23.7 volts I guess battery voltage.
I so I guess I'm at an impasse.
Although I do believe either or both the controller and invertor has a low voltage protection.
What is your SOC on the meter when this happened?
I suspect the inverter is not going thru the shunt and being missed being read by the meter, as per my last post.
I didn't see the SOC when the alarm went off, it was overnight,
I don 't understand this bypassing the shunt, I haven't I don't think.
Correct me if I'm wrong I understood both or either Controller and Invertor have a safety to prevent total draining.
Also would have thought a 2000 watt invertor would handle a 1400 watt HWS cycling in as was already hot from when AC was connected.
The 24 V fridge/house light seem to be wired direct from the controller.