33amps per 100Ah is 0.3CA and 100 amps per 100Ah is 1CA. So it appears they have improved their test conditions, 33amps for 1 hr = 33 Ah or 0.55 amp minutes or 0.55Ah per minute. Multiply that by the 182 mins = 0.55 x 182 = 100.1Ah.cruiserxxx wrote: ↑Sun Jan 21, 2018 2:01 pm The manufacturer specifies 33 amps / 100AH @ 3.2 volts for 182 minutes
At 12.5 volts that load needs to be increased 132 amps for 182 minutes.
So I need to find something that will draw about 1500 watts ...a 240V toaster plus the 325watt fridge comes to mind.
That will also test my wiring for any hotspots and my whole installation....will do that.
Will let you know, Paypal will refund if they are not to specification.
I dont understand the manufacture specifies the dischage test at 33 amps and 100 amps on 100AH, where does .2C test come from cant find it the specifications supplied with the Battery.
Do I have it right the test the manufaturer is specifying between .33C and 1.0C.
The 33 amps @ 12.8v nom. = 422.4w per 100Ah so the 12 cells connected 2P4S will build a 200Ah @ 12.8v nom. battery. This means the load test will need to be 845w, allow roughly 10% loss for the inverter the plugged in load will need to be roughly 760w and a constant load for 182 mins ...... Possibly a 500w and a string of 100w bulbs you can turn off one at a time to hold the load at 66 amps till a cell drops to 2.5v under load. You will need to constantly monitor the cell voltages through the test and stop as soon as a group drops below 2.5v.
If you run the inverter through a Victron BMV, the latest 712 has a Bluetooth output to a computer or smart phone, so the total Ah drawn could be measured, a continuous read out of the load and an alarm set for 12v to give you a warning to go and sit with the battery and watch the cell monitor to catch the 2.5v end of test mark. Set the Victron BMV to a 1.0 Peukert Factor and 100% charge efficiency so the reading will be accurate and you should be set to do a reliable and repeatable capacity test.
I use various watt capacity 12v and 24v water heater elements in a galvanised garbage can full of water as my load with a Junsi 8S running a log and the alarm set to disconnect the load when a cell drops below 2.8v under load and calculate the time x load get the remaining battery capacity. Because the battery bank capacity I need to test can vary between 100Ah and 700Ah the cabling to the heater elements can look a tad agricultural at times and the bigger batteries need me to swap out some of the water every so often to avoid boiling it, but fortunately the voltage curve is reasonably flat once the test is under way so it doesn't require a lot of monitoring. The fall off from below 3v under a 0.5CA load (Winston cell specs) is fairly quick because the capacity is exhausted by that point so I had to build a control to cut the load rather than risk missing it, that gets a tad expensive and not something I want to repeat